I promise this is my last question on propane -
Is it possible to have a 13kg propane oustide in my tiny yard then up the outside of my house to roof / gutter level, in through there in a straight horizontal line to my work room which is 2nd floor/ attic room? The run might be about 12 -15 meters with the last maybe 5 meters going through a small roof space along a wall inside then through an internal plasterboard wall. If its possible would any gas registered plumber be able to do it and would it be horribly expensive? Would metal pipes be better as I read the rubber ones would need replacing frequently?
Thanks
Helen
I think, really, it's a question for a gas registered plumber. My initial thoughts were "it's a lot of piping, and a lot of area for leakage... the most worrying being through the roof space" but as I say, that's initial thoughts. Someone else on the forum may have a similar set up, in which case they can offer you some advice... Or perhaps PM stuwauby... I think it was he who had loads of useful advice on using, and the safekeeping of propane :)
I don't know, but would it lose pressure if it had to travel so far to the torch? They suggest you bleed your pipes for safety and because the gas is dirty at the end of each session, you'd be burning off a lot of gas that way. Having said that I lived in a mobile home for a while (more luxurious fittings than my house) and that ran everything off 2 47kg(?) tanks out the back and the boiler was the other end of the 40ft home to the tanks. Might be worth a call to Calor or a person who can install propane heating; don't think your ordinary gas man would do it, think they have to be certified for all the different things like leccies do.
I will give calor a call in the morning, I did email them yesterday and hoped they might have got back to me today but no reply yet. I just want to understand any potential solution which maybe I should have done before I bought everything!
Thank you all again
Helen
Don't take it up and then down again. A hole in the wall at the lowest level possible is better. Avoid any loops that can trap gas. Many put the pipes though a window and disconnect after each session. Definately NOT inside any wall or cavity.
regards Pete
A lot of people work from their kitchen initially. Is that definitely not an option for you? My sister-in-law and I both had IKEA trolleys, with the torch mounted on that, and we wheeled it to sit under the extractor hood on our respective cookers... Then wheeled the trolley out of the way when it wasn't being used.
Hubby has set it all up for me in my work room, new stainless surfaces and everything but it means working with the propane inside. I have gas leak detector, carbon monocxide detector, fire extinguisher, fire blanket, leak detection spray but still worried and trying to find a way that will make me feel safe. Hubby thinks I'm off my head and being far too cautious because in France his family have used gas (he assures me propane) indoors no problems. Its a 13kg tank, if he got me a smaller one I'd just take it out when I finish and maybe thats the only logical way for me to go
Thanks
Helen
Quote from: Enchanted Cobwebs on November 30, 2010, 06:41:31 PM
Hubby has set it all up for me in my work room, new stainless surfaces and everything but it means working with the propane inside. I have gas leak detector, carbon monocxide detector, fire extinguisher, fire blanket, leak detection spray but still worried and trying to find a way that will make me feel safe. Hubby thinks I'm off my head and being far too cautious because in France his family have used gas (he assures me propane) indoors no problems. Its a 13kg tank, if he got me a smaller one I'd just take it out when I finish and maybe thats the only logical way for me to go
Thanks
Helen
I live in France, and in most houses, unless you're town based, you have propane tanks indoors 24/7 otherwise you couldn't cook. We have a propane tank in the kitchen, in a cuboard beneath the hob as do all the houses in our village. I use butane or my torch though as it's cheaper :)
So he hasnt got the propane thing indoors in France wrong then? Maybe I'm being too cautious. What part of France are you in?
Thanks
Helen
I was going to say use a smaller tank ..
If you look to the top left of your screen, just above where it says visit wiki here in red (and black) there's a FH map, where members can add their details ;D I'm in the Lorraine region, to the north of eastern France (or north east France I guess you could say), bordering Belgium and Luxembourg.
ETA: Just tried the map link and it isn't working (for me anyway... ???)
I think you would be much better off having the tank itself outside and having some kind of permanent plumbed set up. Make sure that you have some form of valve near to your work area where you could just close off the gas if there's a problem.
I agree - call Calor in the first instance or ask a Gas Safe registered engineer (Gas Safe replaced the old Corgi system. I don't know what the law is with respect to bottled gas but no one other than a Gas Safe registered engineer is allowed to connect up mains gas by law, so I guess these would be the best people to ask.
The law in France is NOT necessarily the same as it is in England. It's not necessarily that it's unsafe to have bottled gas in the house, it's probably got more to do with how legal is it and importantly what impact it may or may not have on your household insurance (I don't know the answer to this). And in fact - your chief consideration is not that the gas is in the house but rather more to do with the fact that the gas is required above ground floor.
Anyway - if it were me I would try to get a qualified bod to plumb in a permanent, metal pipe shielded system and have the tank housed out of doors, and then you're away.
What Sal said. Additionally, the gas here is at ground level, and if anything should happen, we have access out of the house. Additionally, the pompiers/firemen will be aware, because of our location, about having gas canisters in the house. Having said all that, the in-laws have had this now for 20+ years and no problems, but insurance requirements are quite likely to be different here. This set-up is a common utility in France... perhaps not so much in the UK... although I'd think quite rural areas probably do the same thing...
My husband is from Lorraine from Domartin les Toul!
I have my 11 kg canister inside. I bleed the pipes after every use and keep my room well ventilated. Havent had any problems or concerns with it. Just be sensible if you have it inside. My folks live in france too and have a propane canister living under the sideboard in the kitchen to run the hobs. They have no probs with it either. Just be sensible and safe in its maintenance. they are fairly sturdy and safe things if treated with due respect TBH.
They talk about plumbing in propane on the US forums (www.lampworketc.com) - doesn't help with the legalities here, but if you just want to see what kinds of thing a set up might involve, have a look over there in the Safety section. From what I remember, definitely metal piping, and you'll want a shutoff valve inside as well as one at the tank. They tend to need two regulators, one outside and one inside which can be adjusted because there's a limit in the US as to the pressure gas coming in through a wall can be. Dunno if we have any similar rules.
Just spoke to calor gas and initially they thought it might be possible but I'd need 19kg minimum and it was only going to be about £300 which although its loads of cash and would buy me bead rollers and glass etc I thought it would be a bargain for peace of mind BUT when they checked they say the torch needs the tank pressure to operate therefore piping it wont work so they cant do it.
They did say calor recommend storage outside although use inside is actually ok especially given the safety measures in place the only remaining risk would be in the event of fire, so, I will use the 13kg tank (if I get chicken I will keep it for the summer and move to the yard till its used up) I will then get the small more portable job and the quick releases and take in and out as needed. Calor thought that was a very good option. I'm going to suggest to Martin that he might discuss that option with newbies like me who ask as I'd have gladly bought the quick releases straight away, now I have to get them and hope I can fit them (scared already!)
I promise I wont ask any more propane based questions, the oxycon seems ok so watch out for my daft questions on another topic!
Thanks all of you a million
Helen
Quote from: Enchanted Cobwebs on November 30, 2010, 08:40:28 PM
My husband is from Lorraine from Domartin les Toul!
90 minutes from us! We're near Longuyon ;D
Quote from: Enchanted Cobwebs on December 01, 2010, 09:55:26 AM
BUT when they checked they say the torch needs the tank pressure to operate therefore piping it wont work so they cant do it.
Helen, what kind of torch are you using? I'm pretty sure we don't run any torches at full tank pressure in the UK (hence the regulators!). Hot Heads were designed to be run at full, but they work on 4 bar (approx 60 psi, I think) and that's how we use them here. Minors and so on run at much lower pressures (up to 5 psi?). Did they say what pressure you'd actually get if they piped it?
Quote from: Kalorlo on December 01, 2010, 12:15:32 PM
Quote from: Enchanted Cobwebs on December 01, 2010, 09:55:26 AM
BUT when they checked they say the torch needs the tank pressure to operate therefore piping it wont work so they cant do it.
Helen, what kind of torch are you using? I'm pretty sure we don't run any torches at full tank pressure in the UK (hence the regulators!). Hot Heads were designed to be run at full, but they work on 4 bar (approx 60 psi, I think) and that's how we use them here. Minors and so on run at much lower pressures (up to 5 psi?). Did they say what pressure you'd actually get if they piped it?
Its a minor, they didnt say what pressure I'd get and as I'm totally ignorant on any of this stuff I just assumed they knew what they were talking about. I did say that the amount of propane being burned isnt huge, but thats probably nonsense to someone who knows their stuff!
I will go back and ask again as I'm sure it wont just be me thats interested. I will get the numbers from them then check maybe with Martin?
Thanks
Helen
Quote from: Billie on December 01, 2010, 12:05:22 PM
Quote from: Enchanted Cobwebs on November 30, 2010, 08:40:28 PM
My husband is from Lorraine from Domartin les Toul!
90 minutes from us! We're near Longuyon ;D
Wow! it really is a small world! We get over that way for family gatherings usually once a year or so, been this year but will drop you a mail before next trip in case you want anything brought over!
We will be retiring to France in a few years but over the other side in Haute Vienne in Bussiere-Poitevine. Huge barn with space for loads of propane outside
Good luck! I had a look at the info about Nortels and it says the recommended operating pressure is 0.25 to 5 psi gas pressure for a Minor.
Quote from: Kalorlo on December 01, 2010, 12:30:51 PM
Good luck! I had a look at the info about Nortels and it says the recommended operating pressure is 0.25 to 5 psi gas pressure for a Minor.
Martin said I need 3 bar, calor say they can only provide 2 bar and that would only be into commercial premises so it wont work. I did give the psi info (thanks for that) also but the answer is still the same - shame
i think i agree with your hubby .....its ok to have it inside whilst torching as long as you are sensible ...and sounds like you have everything in place ...
Quote from: Enchanted Cobwebs on December 01, 2010, 12:25:54 PM
Quote from: Billie on December 01, 2010, 12:05:22 PM
Quote from: Enchanted Cobwebs on November 30, 2010, 08:40:28 PM
My husband is from Lorraine from Domartin les Toul!
90 minutes from us! We're near Longuyon ;D
Wow! it really is a small world! We get over that way for family gatherings usually once a year or so, been this year but will drop you a mail before next trip in case you want anything brought over!
We will be retiring to France in a few years but over the other side in Haute Vienne in Bussiere-Poitevine. Huge barn with space for loads of propane outside
Yes, drop me a line when you're next over. I usually get back to the UK a couple of times to see my mum, and the girls can have some time with nanny ;D I usually do a stock up at Boots each trip if I have the pennies ;D
Quote from: Enchanted Cobwebs on December 01, 2010, 12:58:43 PM
Martin said I need 3 bar, calor say they can only provide 2 bar and that would only be into commercial premises so it wont work. I did give the psi info (thanks for that) also but the answer is still the same - shame
??? In that case I am very confused! Because they're both measuring the same thing (pressure) just in different units. 2 bar is 29 psi...
Quote from: Kalorlo on December 01, 2010, 01:55:13 PM
Quote from: Enchanted Cobwebs on December 01, 2010, 12:58:43 PM
Martin said I need 3 bar, calor say they can only provide 2 bar and that would only be into commercial premises so it wont work. I did give the psi info (thanks for that) also but the answer is still the same - shame
??? In that case I am very confused! Because they're both measuring the same thing (pressure) just in different units. 2 bar is 29 psi...
Guess its a case of it would work just they wont let me have it because I'm not a commercial premises but it might be helpful for anyone who is though they probably already have professionals installing anyway
The bit that really confuses me is that you don't need 2 bar in the first place! 5 psi = 0.34 bar. ???
I don't know why Martin said you need 3 - anyone know if I'm missing something here?
Might he have meant .3 rather than 3?, I phoned him and he did say 3, maybe 2 but say 3 to be on the safe side. I repeated 3 bar and he said yes, 3bar
Quote from: Billie on December 01, 2010, 01:44:19 PM
Yes, drop me a line when you're next over. I usually get back to the UK a couple of times to see my mum, and the girls can have some time with nanny ;D I usually do a stock up at Boots each trip if I have the pennies ;D
I certainly will!
Quote from: Kalorlo on December 01, 2010, 02:04:06 PM
The bit that really confuses me is that you don't need 2 bar in the first place! 5 psi = 0.34 bar. ???
I don't know why Martin said you need 3 - anyone know if I'm missing something here?
Just checked with Martin, he said 3 bar but he meant 0.3 so loads less. I will go back to calor again tomorrow to see if thats achievable. Knowing my luck they will its OK then then wont like the look of the yard, too many windows etc and it will be a no again....
For now the propane is in my workroom, I try not to look at it maybe I will put a curtain around it so only have to look at it when turning on and off! Dont want to spend on smaller tank and quick releases in case this goes ahead
I'm such a scardy cat
Helen
Calor have come back to me again, they can only plumb in propane to domestic property with 0.037 bar which is far lower than needed, so its a definite no to my plan but if you have a commercial premise it would work perfectly for you.
This is the 3rd person I spoke to at calor now who doesnt appear to be horrified that I have the propane indoors and they know its a house and that I have it on the 2nd floor though they did again suggest the best way to go is the smallest tank, quick releases and takle it outside when not in use.